LON card indicates fault (unique name required) when multiple LON cards installed in the JACE-6E, JACE-7, and JACE 8000
  • LON card indicates fault (unique name required) when multiple LON cards installed in the JACE-6E, JACE-7, and JACE 8000
  • RandyDavis
    RandyDavis
  • WaynePeters
    WaynePeters
‎2018-09-06 10:09 AM
Last Updated: Guinan RandyDavis Guinan ‎2023-02-27 07:06 AM
LON card indicates fault (unique name required) when multiple LON cards are installed in the JACE-6E, JACE-7 or Jace 8000
TAC IA Series
  • I/A Series G3, JACE-600, JACE-600E, JACE-700
  • I/A Series N4 JACE 8000
The default name when adding a LON network to the G3/N4 station is LON1.  Both networks will attempt to use the same LON card (LON1) causing a fault condition.
Under each LonNetwork within the Lon Comm Config, specify a unique device name for each card or network (LON1 and LON2).  In the case of the JACE 8000, a total of (4) LON modules is acceptable but would not be advised.  Continue with LON3, and LON4 if required.
  • TAC IA Series
Tags (2)