LED on card reader on ACX57xx (ACX2) flickers when it supposed to be solid green
  • LED on card reader on ACX57xx (ACX2) flickers when it supposed to be solid green
  • SangKim
    SangKim
‎2018-09-06 02:45 PM
  • ACX57XX
  • Some reader types from HID (such as I-class reader).
ACX57XX has new system variables added to get the status of reader connection to controller.(Rdr1Connected ~ Rdr8Connected).
In order to check the Status, ACX57xx checks the voltage presence on the LED channel of each reader port. This function causes the LED of some reader types to flicker at a high frequency.
Set the Rdr1Connected ~ Rdr8Connected system variables to Disabled to keep the LED from flickering.
Tags (3)
  • 3119
  • multi-class
  • multiclass
100% helpful (1/1)