JACE-8000 Serial Ports Inaccessible After Upgrade to N4.9 and Newer

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • JACE-8000 Serial Ports Inaccessible After Upgrade to N4.9 and Newer
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
14230 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

JACE-8000 Serial Ports Inaccessible After Upgrade to N4.9 and Newer

Guinan RandyDavis Guinan
‎2025-05-28 01:04 PM

on ‎2025-05-28 01:04 PM

Issue

Users who clean-dist or factory restore JACE-8000 to Niagara version 4.1 risk losing the serial ports.  

Product Line

TAC IA Series

Environment

I/A Series N4 Jace 8000

Cause

Due to an old defect (fixed in Niagara 4.2 update 2; 4.2.36.38), a programmable device that controls the serial port may be left in an erased state during firmware programming. If this happens, serial ports (COM ports) will be missing when viewing the Serial Port Service under Platform Services in a station. This continues to be an issue for customers who routinely clean-dist or factory reset to Niagara 4.1 on upgrade scenarios. It is not necessary to clean-dist or factory reset when upgrading JACE-8000. If you are advised to do so, it is recommended that you use the 4.9u1 clean dist rather than the 4.1 version one, to avoid being affected by the old defect. 

Resolution

When the JACE-8000 is loaded with Niagara 4.14u2 (or newer) the issue will be automatically detected and fixed on boot. However, when a serial expansion module has been erased, the software cannot distinguish between an RS-232 expansion module versus an RS-485 expansion module. The following messaging will appear in serial shell (and system logs) when the JACE is booting (it will continue booting):

 

Starting USB-0 and USB-1 Host controllers...
Started USB-0 and USB-1 Host controllers
get_ctrlperms: ctrlperms set to 644
Check for usb firmware updates
Re-creating firmware info file in /etc/usb
ERROR: Expansion module info file /etc/usb/350130901TF9S81 is empty, cannot reprogram or start serial ports
       1) To populate the info file with path to appropriate firmware, execute one of following at console command line:
              For RS-485 expansion module: echo "/sys/images/usb/vid03eb/pid2425/Tridium485-2_r01" > /etc/usb/350130901TF9S81
              For RS-232 expansion module: echo "/sys/images/usb/vid03eb/pid2404/Tridium232_r01" > /etc/usb/350130901TF9S81
       2) Reboot to reprogram
Check for usb firmware updates done

 

To fix the issue, download and start PuTTY. In PuTTY Configuration, select the radio button labeled Serial under Connection type. In the text field under Serial line enter COM3 (or whatever the port number is) and enter 115200 in the text field under Speed. Press the Open button to connect. You will need the same VCP driver that is noted in Preparing for new JACE commissioning  and JACE-8000 Backup and Restore Guide.

Sign in to the JACE serial shell. At the prompt type 'sh' to exit the menu and enter serial shell prompt (shell prompt is $ dollar sign).

Copy the correct command from the serial shell instructions. To copy with PuTTY, click and drag over the text. When you lift the mouse button, the text will be in the clipboard. To paste the text, you simply right-click. In the instructions above, 350130901TF9S81 is serial number of a programmable device that controls the serial port. Your serial number will be different. But if that was your serial number, and the erased device was an RS-485 expansion module, then the command to enter would be: 

 

echo "/sys/images/usb/vid03eb/pid2425/Tridium485-2_r01" >

/etc/usb/350130901TF9S81

 

And if it was an RS-232 expansion, then the command to enter would be: 

 

echo "/sys/images/usb/vid03eb/pid2404/Tridium232_r01" >

/etc/usb/350130901TF9S81

 

The file name and path may change in newer versions of Niagara. Therefore, copy from the instructions given in the serial shell output (do not copy the command from this Knowledge Base Article). Press the enter key after the command has been pasted correctly. Then send shutdown to warm-boot the JACE-8000, or just cycle power. 

Observe the following output on the next boot:

 

Starting USB-0 and USB-1 Host controllers...
Started USB-0 and USB-1 Host controllers
get_ctrlperms: ctrlperms set to 644
Check for usb firmware updates
Reprogramming usb device: 1.2 350130901TF9S81...
loaded 350130901TF9S81 with /sys/images/usb/vid03eb/pid2404/Tridium232-1_r07.bin
Reprogramming usb device done: 1.2 350130901TF9S81
Expansion boards have been reprogrammed - rebooting...
exiting usbinit, shutdown requested

 

The JACE will boot one more time, and then it will operate normally.  Please refere to this additonal article for more help.   Jace 8000 Serial Port Issues 
Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • RandyDavis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore