Issue
Product Line
TAC IA SeriesEnvironment
- JACE-645 running I/A Series R2
- G3 Platform Administration used for configuration
Cause
time.properties file for the R2 station on the JACE.Resolution
Manually update the time.properties file on the JACE:
- In G3 Platform, open File Transfer Client and navigate to
/niagara/niagaraR2/sys. - Transfer the
time.propertiesfile to your PC. - Open the file in a text editor (e.g., Notepad), edit the time zone, and save changes.
- Transfer the updated file back to the JACE using File Transfer Client.
- Reboot the JACE and confirm the time zone change in the R2 station.
5. Open the station with R2 and confirm the time zone has been altered as desired.