It is not possible to extract a Menta file from a Xenta programmable
  • It is not possible to extract a Menta file from a Xenta programmable
  • CraigEl
    CraigEl
‎2018-09-07 12:54 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 05:30 PM
It is not possible to extract a Menta file directly from a Xenta programmable. If a backup of the Menta file, or a backup of the Vista database is not available, there is no way to extract the program from the controller.
"File object contain no actual MTA file" when trying to open a Menta file.
TAC Vista
  • Xenta Programmable
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
  • Menta
Going out to a job site without a database backup, or a backup of the Menta applications (.MTA), leaves no way to view the Menta that is running in a Xenta programmable controller.
Options are:
  1. Find a backup of the .MTA Menta application that has been downloaded previously into the controller.
  2. Find a backup of the Vista database.  Menta files are stored in the Vista database for each programmable controller.
    1. To extract a Menta file from a Vista database, the preferred method is described in Get all MTA files saved from a Vista Database.
    2. To extract the files one at a time, right-click on the controller and select Edit.
Connecting to a live controller, it is possible to view all public values inside the controller and to extract a .COD code file.  Unfortunately, these cannot be used to create a .MTA to view the logic.
  • 4797