Dynamic DEMUX Object in R2 LonWorks Jar Displays Incorrect Bit Mapping for SNVT_State
  • Dynamic DEMUX Object in R2 LonWorks Jar Displays Incorrect Bit Mapping for SNVT_State
  • CraigEl
    CraigEl
  • Kim_Baze
    Kim_Baze
‎2018-09-06 10:19 AM
Last Updated: Administrator CraigEl Administrator ‎2025-12-04 11:08 PM
The Dynamic DEMUX object in the R2 LonWorks jar (Conversions folder) appears to incorrectly set output bits for certain SNVT_State values, causing confusion when interpreting state information.
TAC IA Series
Niagara R2(all versions)
The discrepancy occurs because some third-party manufacturers define SNVT_State bits starting from bit15 on the left, counting down left to right. In contrast, the Dynamic DEMUX object assigns bits from bit0 to bit15, with bit0 on the left and counting left to right.
  • Understand the bit assignment logic used by the Dynamic DEMUX object:
    • For example, a SNVT_State value of 1000 hex equals 1000000000000000 in binary.
    • The DEMUX object interprets this as bit0 ON.
  • If third-party documentation indicates bit15 ON for the same value, this is due to their reversed bit numbering convention.
  • Once this difference is understood, interpret DEMUX output bits accordingly.