Issue
- Alarms stops coming into Vista from Xenta 280/300/401 in the Lonworks network under a Xenta 913 or a Xenta 701.
- Xenta 280/300/401 controller goes offline/online in Vista.
- Unable to disable an alarm from a Xenta 280/300/401 that are under a Xenta 913 running as Xenta Server in Vista.
Product Line
TAC Vista
Environment
- TAC Vista
- TAC Xenta 913
- TAC Xenta 701
- TAC Xenta 401
- TAC Xenta 301
- TAC Xenta 302
- TAC Xenta 281
- TAC Xenta 282
- TAC Xenta 283
Cause
There is no support for adding Xenta 280/300/401 to the Lonworks network under a Xenta 913/Xenta 701 running as Xenta Servers in Vista (even though if it is possible to do it in the software).
Resolution
Use a different Xenta Server that supports adding programmable Xenta controllers in the Lonworks network.
Please see the table in chapter 1.1 of the TAC Xenta Server - Networks Technical Manual or Xenta Server version 5.1.5 and after Major Features.