Issues with programmable Xenta controllers in a Lonworks network under a Xenta Server
  • Issues with programmable Xenta controllers in a Lonworks network under a Xenta Server
‎2018-09-10 11:02 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:50 AM
  • Alarms stops coming into Vista from Xenta 280/300/401 in the Lonworks network under a Xenta 913 or a Xenta 701.
  • Xenta 280/300/401 controller goes offline/online in Vista.
  • Unable to disable an alarm from a Xenta 280/300/401 that are under a Xenta 913 running as Xenta Server in Vista.
TAC Vista
  • TAC Xenta 913
  • TAC Xenta 701
  • TAC Xenta 401
  • TAC Xenta 301
  • TAC Xenta 302
  • TAC Xenta 281
  • TAC Xenta 282
  • TAC Xenta 283
There is no support for adding Xenta 280/300/401 to the Lonworks network under a Xenta 913/Xenta 701 running as Xenta Servers in Vista (even though if it is possible to do it in the software).
Use a different Xenta Server that supports adding programmable Xenta controllers in the Lonworks network.
Please see the table in chapter 1.1 of the TAC Xenta Server - Networks Technical Manual or Xenta Server version 5.1.5 and after Major Features.
  • 7603