Issue
Product Line
TAC IA SeriesEnvironment
- I/A Series R2 Enterprise Server
- I/A Series R2 UNC
Cause
Resolution
-
Schedule Configuration
- Place master schedule objects in the Enterprise Server and slave schedule objects in UNC controllers.
- Link
masterOutfrom the Enterprise Server schedule tomasterInof one or more UNC schedule objects. - Each UNC retains schedule data locally for resilience during communication failures.
-
Calendar Configuration
- Place master calendar objects in the Enterprise Server and slave calendar objects in UNC controllers.
- Link
masterOutfrom the Enterprise Server calendar tomasterInof one or more UNC calendar objects. - Each UNC retains calendar data locally for resilience during communication failures.
-
Holiday Override Linking
- Link the local calendar’s output to the local schedule’s holiday override input (e.g., master calendar → master schedule or slave calendar → slave schedule).
- Do not link holiday overrides across the network.
- Ensure holiday schedules are not left blank; otherwise, outputs may remain active.