Issue
Can the remote sensor with override switch (SE3020W1045) be interfaced to a SE7600H5045B and be accessed via a BACnet integration? The override switch is a trigger to provide cooling to the area served.
Product Line
EcoStruxure Building Expert
Environment
SmartStruxure Lite
Cause
Provide end user a simple way to get comfort cooling
Resolution
Interface the override switch to DI 01 on the SE7600H5045B. It will then be accessible via BACnet to trigger comfort cooling.