Issue
Can a door switch input be configured to operate without the input resistor?
Can supervised inputs be configured to work without an input resistor?
Environment
- NetController
- ACX5720
- ACX5740
- AC_1
- AC_1 Plus
Cause
When designing or troubleshooting a security access job, it is important to know if the hardware requirements are absolutely mandatory.
Resolution
- Within the Continuum door object class, the input type is not selectable - it is a supervised input.
- As supervisory inputs they require an input resistor to be installed.