Input (UI4) XP expansion module attached to BCX not updating.
  • Input (UI4) XP expansion module attached to BCX not updating.
  • BillNeville
    BillNeville
‎2018-09-06 01:34 PM
InfinityInput (digital) not changing value when dry contact on relay changes state.
Tried disabling and changing value but will not change.
On bacnet side the point is set to out of service and will not change.
New input points created on the UI4 are also out of service on bacnet side and will not change.
Tried powering down expansion module - no luck.
Tried deleting point on Infinity side and saving to database on bacnet - works fine. But when recreating the input, comes up the same way.
bCX, 4040, bCX4040,
XP Expansion Module UI4, UI-4
  1. Replace UI4 with bCX powered off.
  2. Delete the point on Infinity side, save controller to database on Bacnet side.
  3. Drag & drop input from another bCX on Infinity side.
  4. Save to database on Bacnet side. Point starts updating and is no longer out of service.
See also
  • 5653