Indication a remote I/O module (MNB-1000-15) is offline when used with a Tridium JACE
  • Indication a remote I/O module (MNB-1000-15) is offline when used with a Tridium JACE
  • RandyDavis
    RandyDavis
  • Kim_Baze
    Kim_Baze
‎2018-09-06 01:04 PM
Last Updated: Guinan RandyDavis Guinan ‎2023-07-13 10:05 AM
When a remote I/O module goes offline the JACE will show an "NA" for the analog inputs but the binary inputs from a remote I/O module still show maintain their last value.
TAC IA Series
  • I/A Series MNB 1000-15
  • I/A Series JACE
The BIs from a remote I/O module that is offline are going to an "NA" status if viewed from WorkPlace Tech.  At the JACE an "NA" received from a BI object will be interpreted as a "fault" and the object will show its last value and turn orange to indicate it is in fault.
When a Remote I/O module is off-line its AI and BI outputs will show as NA in WorkPlace Tech.
At the JACE an "NA" received from a BI object will be interpreted as a "fault" and the object will show its last value and turn orange.  The BI can be set up to annunciate an alarm based on the fault condition in the JACE if necessary.
  • TAC IA Series
Tags (2)
  • 6603
  • RandyDavis23