How do you define the number of decimal places displayed for a point?
Is it possible to change the number of decimals displayed in WorkStation / WebStation?
  • Building Operation WorkStation
  • Building Operation WebStation
The operating system's regional settings determine the default resolution for decimal places displayed. This value cannot be modified within WorkStation; however, the regional settings in WebStation can be adjusted to show the desired number of decimal places.
This setting applies to all displayed values except graphics, where the graphic editor can define the number of digits displayed.
WorkStation
  1. Open Control Panel
  2. Select under Clock and Region - Change date, time, or number formats
  3. As shown in the screenshot below, select Additional Settings [1]
  4. Then adjust the Customize Format "No. of digits after decimal to your requirements" [2].
  5. Restart WorkStation if already opened.
WebStation
  1. From the User Account drop down
  2. Select Settings
  3. Select Regional
  4. Change the Decimals from Auto to the desired number (0-6) required in WebStation. 
  5. Click Save
  6. Log off/on to WebStation to see these changes. 