Import/Export in TAC Vista Workstation does not work

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Import/Export in TAC Vista Workstation does not work
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Jonas_Brissman
    Jonas_Brissman
  • Benji
    Benji
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1955 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Import/Export in TAC Vista Workstation does not work

Picard Product_Support
‎2018-09-06 01:00 PM

Issue

Import/Export in TAC Vista Workstation does not work. Nothing happens when trying to start the import/export.

Environment

TAC Vista

Cause

The $DatabaseExport and $DatabaseImport objects in the Vista database has been removed, probably during an upgrade.

Resolution

In the instructions below, we assume that TAC Vista is installed in the default location. Replace the version number (5.1.6) with the actual version you have installed, and the Vista Server name (VistaServer) with the actual name of your Vista Server.

This procedure requires that TAC Vista Server is running as an application, and not as a service.

1. Make sure TAC Vista Server is stopped

-- First we need to change a file to allow creation of these objects --

2. Browse to C:\Program Files\Schneider Electric\TAC Vista 5.1.6\$cfg

3. Find a file named "objtmpl.cfg", make a copy, just in case.

4. Edit the file with notepad and find the strings FI_EXPORT and FI_IMPORT.

5. Remove AB on each of the two lines, (stands for abstract object), save and close.

6. Browse to the TAC Vista database folder, and open the folder $thisdb.

7. Change the name of the file TacVista.cfg, to TacVistaOld.cfg

8. Start TAC Vista Server.

-- Now we need to create the missing objects --

9. Open the testclient (testclt.exe) located in the folder C:\Program Files\Schneider Electric\TAC Vista 5.1.6

10. In the menu, click "Session-->Log in"

11. In the menu, click "Services-->Create"

12. In the ID field, write "VistaServer-DatabaseExport" and in the type field write "FI_EXPORT"

13. Click "Create".

14. In the ID field, write "VistaServer-DatabaseImport" and in the type field write "FI_IMPORT"

15. Click "Create".

-- Now we have to change the name of the created objects to $DatabaseExport and $DatabaseImport --

16. In the menu, click "Services-->Access"

17. In "Enter ID:" write "VistaServer-DatabaseExport.$name"

18. Click "Request"

19. Write "$DatabaseExport" in the "New Value" field, and click "Poke".

20. In "Enter ID:" write "VistaServer-DatabaseImport.$name"

21. Click "Request"

22. Write "$DatabaseImport" in the "New Value" field, and click "Poke".

23. Reenter AB on each of the two lines in "objtmpl.cfg" previously edited in step 4, save and close.

 
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6865
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of