Issue
When the time is changed on any TAC Xenta unit using the TAC Xenta OP, all TAC Xenta devices in that group will have their time changed by the same amount.
Product Line
TAC Vista
Environment
- TAC Xenta Programmable Controllers
- TAC Xenta Group
- TAC Xenta OP
Cause
The time parameters will be considered during this broadcast. This occurs when you change ANY controller, not just the group master.
Resolution
For example, the time is changed on one controller. It will add the minutes in its time zone field and broadcast the time as GMT. The other controllers in the group will receive the message, subtract their time zone minutes, and change their own time.