How to connect a Modbus TCP device to the IC3-MODBUS controller.
Satchwell BAS & Sigma
Sigma IC3-MODBUS
The Modbus device uses a TCP/IP interface instead of traditional RS-232 or RS-485 serial communication.
To establish communication between the IC3-MODBUS controller and a Modbus TCP device:
  1. Single IP Connection
    The IC3-MODBUS controller requires only one IP connection. This connection supports both:
    • The Sigma interface
    • The Modbus TCP interface
  2. Network Configuration
    The Modbus TCP device must also be connected to the same IP network as the IC3-MODBUS controller.
  3. IP Address Mapping
    • The IP addresses of both the Modbus controllers and the Modbus TCP devices must be defined.
    • These mappings are configured in the gateway.txt file located in the Sigma system.
  4. Firmware Reference
    For detailed setup instructions and compatibility, refer to:
    • Sigma Release 4.06 - Firmware IC3-Modbus Release Note