Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

IC GEN OPC and XML-DA Data Type Compatibility

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • IC GEN OPC and XML-DA Data Type Compatibility
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1892 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

IC GEN OPC and XML-DA Data Type Compatibility

Picard Product_Support
‎2018-09-07 11:36 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-06 04:21 PM

Issue

Can the IC GEN OPC Server communicate with an OPC XML-DA server?

Product Line

Satchwell BAS & Sigma

Environment

  • IC GEN OPC Server
  • Third-party OPC Clients
  • OPC DA and OPC XML-DA protocols

Cause

The IC GEN OPC Server is designed to support OPC DA (Data Access) only. It does not natively support OPC XML-DA, which is a different protocol standard used by some third-party OPC servers.

Resolution

To enable communication between the IC GEN OPC DA client and a third-party OPC XML-DA server, a protocol translation gateway is required.

Recommended Solution:

Use a third-party gateway from Advosol, which acts as a bridge between OPC DA and OPC XML-DA. This allows the IC GEN OPC DA client to access data from XML-DA servers.

  • For more information and to obtain the gateway, refer to Advosol’s OPC XML-DA Gateway (external link).

Configuration Example:

In the IC GEN OPC gateway.txt configuration file, reference the third-party OPC XML-DA server using the following format:

Item0=4^IndigoVision^192.168.246.95^Fromlv.analysis.motionalarm1^0

Explanation of fields:

  • IndigoVision: Name of the third-party OPC XML-DA server
  • 192.168.246.95: IP address of the server
  • Fromlv.analysis.motionalarm1: OPC item path
  • 0: Item index or priority (as required by IC GEN)

Additional Notes

  • Ensure the third-party gateway is installed and configured correctly on a supported operating system.
  • IC GEN OPC version 4.05 or later is recommended for compatibility.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 5108
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore