I/NET will run in application mode, but will quickly shut down when in service mode
TAC INET
  • I/NET Configuration Profile
  • I/NET Seven
The I/O Server can be configured to auto shutdown whenever the I/NET Workstation application is closed. If this setting is used, the service will stop whenever I/NET Workstation is closed as well.
  1. Open the I/NET Configuration application. [Start>All Programs>I/NET>INET Config]
  2. Click on the Radial button so that I/O Server is maintained when no clients are present. Do NOT use the shutdown option when using I/NET as a service
  • TAC INET