Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

I/NET MSDE to Full SQL

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET MSDE to Full SQL
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • sesa139513
    sesa139513
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1464 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET MSDE to Full SQL

Picard Product_Support
‎2018-09-10 11:06 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:36 PM

Issue

MSDE to Full SQL

Product Line

TAC INET

Environment

I/NET Seven site

Cause

Need to Move db from MSDE to Full SQL

Resolution

Below are the steps to move from your MSDE to a full SQL instance:

  1. Make sure your version of I/NET supports Full SQL (check ReadMeSeven.txt file located on the Install CD)
  2. Backup all controllers (HVAC and Security) to database
  3. Backup MSDE database using DBCreate (Start, Programs, I/NET, DbCreate Utility)
  4. If running I/NET as a service, unregserver to stop the service (Running I/NET Seven as a service on Windows)
  5. If applicable, demote Equalized Clients(EQ) to StandAlone then demote FileMaster(FM) to Standalone
  6. Using Microsoft SQL Management Studio Express create an instance database for INETSeven which I have explained how to do in step 7
  7. In SQL Management Studio Express right click on Databases and select New Database and be sure to name specifically INETdb
  8. Using I/NET DbCreate Utility when the login screen appears, connect to the SQL Server (Computer Name Required) you want to use which has full SQL
  9. Create a blank I/NET SQL database with proper login credentials
  10. Still from DBCreate Utility, restore the database from previous step which is a good backup
  11. Re-install I/NET over the top of the existing install so that the StandAlone will use this instance of SQL
  12. Have the proper security key information
  13. When the install gets to the SQL, select the instance from the SQL database created in step 9
  14. Complete the installation
  15. Suggested reboot if necessary and start I/NET
  16. Restore SAV files (which is the database, see How to upgrade bin and SAV files in I/NET controllers) to the controllers in the I/NET network so everything is in sync with the db
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 8026
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of