I/NET Door Processing Unit (DPU) Offline
  • I/NET Door Processing Unit (DPU) Offline
  • sesa139513
    sesa139513
  • Roger_Bently
    Roger_Bently
‎2018-09-06 10:59 AM
Last Updated: Administrator DavidFisher Administrator ‎2019-08-12 06:15 AM
DPU Offline shows up when the Door Configuration is selected from the Summary Controller.
TAC INET
All versions of I/NET
The Resident I/O Points for those doors are either non existent in the save file, offline or have lost communications to the controller.
  1. Verify that the DPUs are Online and communicating to the Controller by clicking connect
  2. Controller/MCU Configuration and verify that the addresses are blue and communicating
  3. Select Resident I/O Points and verify that the 08 and 09 points does exist for the respective points
  4. If not add and then update the database
  5. Select Summary/Door Configuration/ and verify that the doors are now in blue rather than red indicating that they are online.
Temporary Individuals have the DPU RES check box, which means the information is stored in the DPU (such as a SCU) until the battery runs out.
  • TAC INET
  • 11473