I/NET Direct Digital Control (DDC) Modules

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET Direct Digital Control (DDC) Modules
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
8542 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET Direct Digital Control (DDC) Modules

Picard Product_Support
‎2020-09-15 04:18 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:47 AM

Issue

A more in-depth description of each of the Direct Digital Control (DDC) modules in I/NET

Product Line

TAC INET

Environment

  • I/NET DDC
  • DCUs, PCUs, MRs
  • Two Position Module (2POS)
  • PID Controller (PID)
  • Float Module (FLT)
  • Reset Module
  • DDC Hi/Lo Module (HI/LO)
  • Relay Module (Single Pole Double Throw Relay)
  • Calc Module

Cause

DDC is a system that measures a variable, compares the variable with a known value to determine the error, processes the error using a specific software algorithm, and then produces an output to modify the controlled variable.

Resolution

Most of these modules are discussed in both TCON 083 or  TCON 299 System Operator Guide for more details. (The System Operator Guide is installed by default on your I/NET Host Workstation)


DDC Two Position Module (2POS)

Ddc_pos.pngThis module is used where the final control element is in either one state or another opposite state (ON/OFF, OPEN/SHUT). This type of control will commonly be used for simple heating or cooling systems, starting and stopping motors, controlling water sprays for humidification, etc. This module is available in our PCUs and DCUs; and you can customize it for your needs. 

DDC PID Controller (PID)

Ddc_pid.pngIn Proportional (P), Proportional + Integral (PI), and Proportional + Integral + Derivative (PID) control, the control element moves linearly to a position that is proportional to the deviation and the rate of deviation of the controlled process variable from a prescribed setpoint. This type of control, in any of its three modes, or combinations thereof, is commonly used for the control of modulating valves, vanes or modulating motors where a proportional output control point is used. The proportional output control point may be either an analog output (voltage, current, resistance) or a pulse width output where the duration of the pulse is proportional to the error variation. This module is available in our PCUs and DCUs; and you can customize it for your needs. 

DDC Float Module (FLT)

Ddc_flt.pngTraditionally, floating control actuates a control device when the error, i.e. the difference between the controlled process variable and the setpoint, exceeds a deadband and maintains the control until the error is within the deadband. The floating controller is based on the same principle however it has been enhanced to include PID control without the requirement for analog output or pulse width position feedback. The output of this controller may be directed toward either a pair of variable pulse width discrete outputs to control a bi-directional drive motor or dual EP value arrangement which is generally described as a "pressure-vent" controller. This type of control is commonly used for the same applications as the PID controller where positive feedback is either unnecessary or economically unsound. This module is available in our PCUs and DCUs; and you can customize it for your needs. 

DDC Reset Module (RESET)

Ddc_Reset.pngReset is used to develop a setpoint output in an inversely or directly proportional relationship to one or two analog inputs and one or two operator-specific reset schedules. This module is available in our PCUs and DCUs; and you can customize it for your needs. 

DDC Hi/Lo Module (HI/LO)

Ddc_hilo.pngThis module is used to provide the highest and/or lowest value from two or more measured variables, most commonly temperatures. HI/LO can be cascaded to accommodate virtually any number of inputs of similar nature. Typically the lowest space temperature would be the most logical to use to directly reset the heating water setpoint. The HI/LO modules provide the control engineer with a convenient alternative method for making the selection. The HI/LO modules may also be used as an OR/NOR selector by using the state(s) of various monitored discrete points. This module is available in our PCUs and DCUs; and you can customize it for your needs. 

DDC Relay Module (Single Pole Double Throw Relay)

Ddc_Relay_Module.pngThis module provides a mechanism for selecting one of two values or states based on conditions within the controlled environment. The actions of the relay are controlled by one discrete input and control which of two input states or values is directed to the output. The inputs and output may be either discrete or analog. The actions of this relay are analogous to its electric/electronic counterpart in its simplest form. This module is available in our PCUs and DCUs; and you can customize it for your needs. 

DDC Calc Module

Ddc_calc.pngThis module functions similarly to calculations added to a point through the calculation extension editor. This module is only available in Micro Regulators (MR). It is not available in Application Specific Controllers (ASC). 

Labels (1)
Labels:
  • TAC INET
Tags (6)
  • Find more articles tagged with:
  • 1556
  • ahu
  • inet
  • reprogram
  • RobertAndriolo20
  • shutdown
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore