I/NET Configuration Status parameters: Processor Loading and LAN Loading (Percentages (%))

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET Configuration Status parameters: Processor Loading and LAN Loading (Percentages (%))
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2034 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET Configuration Status parameters: Processor Loading and LAN Loading (Percentages (%))

Picard Product_Support
‎2020-10-13 03:17 PM

on ‎2020-10-13 03:17 PM

Issue

Processor % Loading and LAN % Loading; What do these mean and how can they impact my system.

  • Processor % Loading -  This field displays the Controller processor (CPU) percent loading (0–100%). This number is an indication of how busy the controller is. 
  • LAN % Loading - This shows the percentage of controller LAN communication attributable to this controller only. It is not the total control LAN loading figure.

Product Line

TAC INET

Environment

ALL I/NET Controllers (Controller LAN (CLAN) based)

Cause

A greater understanding of the values seen at each controller can greatly assist in having a more efficient I/NET network.

Resolution

The controller Processor % loading and LAN % loading are available from each controllers' configuration/status editor.

  • You must be connected to the controller in order to use this editor. This information can also be obtained using the hand-held console, Code 3 (CPU %), and Code 4 (LAN %).
  • These fields are display only. You cannot make changes. However, you can make changes to the database and observe the relative loading statistics after.
  • The readings should be taken with all graphic pages and DCU controller point summaries closed.

Processor % Loading

This field displays the Controller processor (CPU) percent loading (0–100%).  This number is an indication of how busy the controller is.  If this number is 100, control actions may be lost or delayed.

You should not let this reading go above 80%.  If kept to below 80% then if the processor peaks for some reason, it has 20% to peak in without locking up for a number of processor machine states.

The conditions that affect the processor loading are as follows:

  1. Resident Point scan interval.  All resident points are processed by the firmware.  If you find that the processor loading is high, then edit all the AOs and DOs that do not have a calculation extension and adjusting the scan intervals to 255 seconds.  In heavily populated controllers this will bring down the processor % loading somewhat.
  2. Calculated Point frequency.  All resident points with a calculation extension will have their calculation processed at the scan interval of the target point.  If you find that the processor loading is high, then, on the calculation extensions that perform less important tasks, you may edit the target point’s scan intervals to a larger figure.
  3. Event Initiated Sequences.  A number of sequences that are in a loop, that is to say, running sequences with a skip back to themselves causing the sequence to run continuously, will cause the processor % loading to rise.  Edit and modify to create a more efficient database.  Ensure that a minimum of 1-second delay is implemented between each action within a sequence.  Do not leave all actions at the default value of zero.  
  4. DDC Module Sample Interval.  All DDC modules are processed at their respective sample interval.  If you find that the processor loading is high, then, on the DDC modules that perform less important tasks, you may edit the DDC module’s sample rates to a larger figure.
  5. Global or Indirect Traffic.  Naturally, large quantities of global and or indirect traffic to and from the controller will cause the processor % loading to rise.  See the next section “LAN % Loading” for more details.
  6. Graphic Pages and or Controller Point Summaries.  Graphic pages and or controller summaries with large quantities of points requesting information/data (solicited messages) from a controller will cause the processor % loading to rise.  This also includes the number of pages open either on the one host or multiple hosts.  You have a number of choices here; you could increase the host’s “Monitor Refresh Interval” to minimize the solicited traffic or you could rationalize the graphic pages to a more efficient use of points.
  7. Alarm or Messages.  Large quantities of alarm or message traffic (unsolicited messages) from the controller will cause the processor % loading to rise.  You will have to identify the cause.  Be aware just taking out the matching message masks from the host or from the point will not inhibit the message from transmitting to the LAN, the Resident Point’s Message and or Alarm priority must be set to “None”.
  8. SEVENTRENDS Data Uploads.  Large quantities of SEVENTRENDS data (unsolicited messages) being uploaded to the LAN from the controller will cause the processor % loading to rise.  You will have to identify the origin and alter the “Cell Sample Counts” and or the “Sample Control Interval” to relieve the condition.  Be aware just taking out the Host SEVENTRENDS Cell mask or the point’s Trend Sample SEVENTRENDS Distribution Mask will not inhibit the data from transmitting to the LAN, the SEVENTRENDS Distribution Priority must be set to “None”.

 LAN % Loading

This shows the percentage of controller LAN communication attributable to this controller only.  It is not the total control LAN loading figure.  Treat the control LAN as a 100% resource.  If this controller has a LAN percent loading of 23%, then the control LAN has only 77% of resources left to service the other controllers on the control LAN.

Another way to look at it is, in the above example, out of every 100 token passes on the control LAN this controller has used the token 23 times.

The best scenario is to have the lowest figure possible, e.g. 0%.  Just imagine a control LAN with 25 controllers connected, each controller with a ‘LAN % loading’ of 5 %.  The LAN is flooded and will cause messages to be lost and or buffered, graphic pages will not update as expected and the system will dramatically slow down.

The empirical rule is as follows: The ‘LAN % loading’ is allowed to rise to a figure above 0%, but within 20 seconds, it must go back to 0%.

The conditions that affect the ‘LAN % loading’ are as follows:

  1. LAN Reconfigures.  Every time a LAN reconfigures all global points in every controller on that control LAN transmit their values on to the LAN, and all indirect points request, at their scan interval, an update from their associated global points.  On an unstable control LAN, this could contribute heavily to a controller’s ‘LAN % loading’.
  2. Global Point Traffic.  Large quantities of global point traffic from the controller will cause the ‘LAN % loading’ to rise.  The conditions that affect the frequency of global traffic are:
    1. Global point’s “Broadcast Change Counts”.  Remember that multiplying the analog point’s conversion coefficient’s ‘m’ value with the broadcast change count value will be the resolution of the analog value to be exceeded to cause a broadcast onto the LAN. Just imagine a globalized analog point with a ‘m’ value of .05 and a Broadcast Change Counts set at 1.  Then this sensor will globalize its value every time the value exceeds 0.05 creating globalized traffic.
    2. The faulty sensor being globalized.  The sensor’s value being unstable to the extent that the point’s value changes exceed the “Broadcast Change Counts”, in extreme cases creating globalized traffic.
    3. Controller’s Power Line Frequency, HHC function [Ctrl 92], not set correctly.  This is for setting a notch filter to filter out power supply noise being imposed over the sensor’s input signal thereby helping to eliminate the sensor’s value appearing to fluctuate.  These fluctuations could send a global sensor’s value change to exceed the “Broadcast Change Counts” in extreme cases creating globalized traffic.
    4. Pulsed Input (PI) points.  The PI points “Scans between Broadcast” incorrectly assigned.
      Beware: a PI point with a “Scan Interval” of 1 second and a “Scans between Broadcast” set at 1 second will cause the controllers ‘LAN % loading’ to rise by 10% and stay there, even though the PI point’s value may not have changed.
  3. Indirect Point Traffic.  Large quantities of indirect point traffic from the controller will cause the ‘LAN % loading’ to rise.  The conditions that affect the frequency of indirect point traffic are:
    1. LAN Reconfigures.  Every time a LAN reconfigures all indirect points, at their scan interval, request an update from their associated global points.  On an unstable control LAN, this could contribute heavily to a controller’s ‘LAN % loading’.
    2. Indirect Point scan intervals set incorrectly.  If an indirect point does not see a change in its state/value from the global point after 2 scan intervals then the indirect point will request an update from its associated global point to be reported at the indirect point’s 3rd scan.  With global points that are reasonably static, i.e. not altering a lot e.g. status points, etc., the associated indirect points will carry out their requests for updates.  Therefore the indirect points scan intervals should be staggered system-wide, not just controller-wide.  If all the indirect points have the same scan interval they could conceivably request at the same time and queue and hang onto the control LAN’s token.
  4. Graphic Pages and or Controller Point Summaries.  Graphic pages and or controller summaries with large quantities of points requesting information/data (solicited messages) from a controller will cause the ‘LAN % loading’ to rise.  This also includes the number of pages open either on the one host or multiple hosts.  You have a number of choices here; you could increase the host’s “Monitor Refresh Interval” to minimize the solicited traffic or you could rationalize the graphic pages to a more efficient use of points.
  5. Alarm or Messages.  Large quantities of alarm or message traffic (unsolicited messages) from the controller will cause the ‘LAN % loading’ to rise.  You will have to identify the cause.  Be aware just taking out the matching message masks from the host or from the point will not inhibit the message from transmitting to the LAN, the Resident Point’s Message and or Alarm priority must be set to “None”.
  6. SEVENTRENDS Data Uploads.  Large quantities of SEVENTRENDS data (unsolicited messages) being uploaded to the LAN from the controller will cause the ‘LAN % loading’ to rise.  You will have to identify the origin and alter the “Cell sample counts” and or the “Sample Control Interval” to relieve the condition.  Be aware just taking out the Host SEVENTRENDS Cell mask or the point’s Trend Sample SEVENTRENDS Distribution Mask will not inhibit the data from transmitting to the LAN, the SEVENTRENDS Distribution Priority must be set to “None”.
     
Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 5490
  • RobertAndriolo20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore