I/NET Alarms and Events to SNMP Clients
  • I/NET Alarms and Events to SNMP Clients
  • sesa139513
    sesa139513
  • Roger_Bently
    Roger_Bently
‎2018-09-06 02:59 PM
Need to deliver I/NET alarms and events to a third party SNMP client
I/NET site
Desire to deliver alarms/events to third party
There are two mechanisms in the Xenta 527 related to SNMP:
  1. MIB - sends a block of data about the status of the I/NET system, LAN re-config, loading etc.
  2. SNMP traps - use filters to look at the incoming message stream from I/NET or any other connected system to capture specific messages and send them as alarms to an SNMP server.
The default configuration for a Xenta 527 out of the box has alarms enabled but events disabled. There is a check box in the 527 Config Screen that turns this on/off.
To change this:
  1. Go to your project
  2. Add Page/SNMP Trap Page
  3. Right click on SNMP Trap Page
  4. Select SNMP Trap Filter
  5. Select Status
  6. Check the Event check box.
  • TAC INET
  • 2548