Issue
Product Line
TAC IA SeriesEnvironment
- I/A Series R2 SNMP integration
- I/A Series G3 SNMP integration
Cause
The issue occurs because different versions of I/A Series use different MIB files.
- R2 requires TridiumR2-MIB (introduced in version 2.301.528 and above).
- G3 uses TridiumR3-MIB.my for versions 3.4 and earlier.
- From G3 version 3.5 and above, MIB files can be generated locally in Workbench.
Resolution
- Verify the I/A Series version:
- R2 (≥ 2.301.528) → Use TridiumR2-MIB.
- G3 (≤ 3.4) → Use TridiumR3-MIB.my.
- For G3 version 3.5 and above:
- Use Workbench’s right-click menu on the local SNMP device to generate a MIB file.
- Refer to Niagara AX 3.5 SNMP Driver Guide, pages 3-17 to 3-21 for details.
- To view the MIB file in Workbench:
- Navigate to File > Open > Open Ord or press Ctrl + L.
- Enter:
local:|module://snmp/tridiumMib/TridiumR3-MIB.my
- Ensure the correct MIB file is provided to the third-party system.