Issue
Product Line
TAC IA SeriesEnvironment
- I/A Series R2 software releases: 522.v2, 529, 532
- Enterprise Server (ES) or UNC-based stations
- Access via Microsoft Internet Explorer (IE 7/8 or later with security updates)
Cause
Microsoft Internet Explorer security updates changed how ActiveX and third-party Java applets are initialized.
- IE now requires explicit user activation (click-to-activate) for embedded applets.
- This behavior blocks Niagara R2’s Java-based graphic components, preventing proper rendering.
- Java security prompts may also appear due to stricter applet execution policies.
Resolution
Apply the workaround introduced in R2 522.v2 to disable IE’s ActiveX activation fix:
- Backup station database before changes.
- Open Admin Tool → Host → Edit File → System Properties.
- Append the following lines at the end of
system.properties(do not remove#comments):# This is used to disable the IE ActiveX activation fix. If set to # false, then the user will be required to click on the# false, then the user will be required to click on the applet # before he is able to interact with it (only effects IE users). ie.activex.activation=false - Save the file and restart the station (or reboot the UNC/ES).
- Repeat steps for Enterprise Server and UNCs as needed.
Additional Notes / Best Practice
- This workaround only applies to Internet Explorer; modern browsers do not support R2’s ActiveX/Java graphics.