I/A Series R2/G3 Web Graphics Blocked or Security Warnings After Java Updates

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series R2/G3 Web Graphics Blocked or Security Warnings After Java Updates
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1132 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series R2/G3 Web Graphics Blocked or Security Warnings After Java Updates

Picard Product_Support
‎2018-09-11 04:26 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-03 04:28 PM

Issue

When accessing I/A Series R2 or G3 station graphics via a web browser, graphics fail to load or repeated Java security warnings appear. Common symptoms include:

  • “Application Blocked by Security Settings”

  • “Your security settings have blocked an application from running with an insecure or expired JRE.”
  • Popups warning of security vulnerabilities for each Java applet.

  • In Firefox: “This plugin has security vulnerabilities. Click here to activate the Java(TM) Platform SE Plugin.”

Product Line

TAC IA Series

Environment

  • I/A Series R2
  • I/A Series G3

Cause

Oracle introduced stricter Java security controls starting with Java 7 Update 11 and further tightened them in Update 51 and later.

  • Unsigned or self-signed applets are blocked by default.
  • Known vulnerabilities in older Java versions trigger warnings.
  • Browser plugins (IE, Firefox) enforce additional security prompts.

Resolution

Several approaches exist depending on site security policy:

Option 1: Use Java Exception Site List (Recommended for Java 7u51+)

  1. Open Control Panel → Java → Security.
  2. Ensure Security Level is High (or Medium if required).

    CraigEl_0-1764807740942.png

  3. Click Edit Site List… → Add.
  4. Add URLs for all I/A Series servers and controllers:
    • http://<EnterpriseServer-host-or-IP>
    • http://<UNC-or-JACE-host-or-IP>

    • Confirm changes and restart browser.

Option 2: Adjust Java Security Level (Legacy Workaround)

  • For Java 7 Update 17 or earlier:
    1. Open Java Control Panel → Security tab.
    2. Set Security Level to Medium or Low (not recommended for high-security environments).

    3. Restart browser.

Option 3: Downgrade Java (Last Resort)

  • Testing shows Java 7u9 does not trigger prompts in IE9.
  • Downgrade only if site policy allows and system is isolated.

Option 4: Browser-Specific Workarounds

  • Internet Explorer: Click Run on each security prompt.
  • Firefox:
    • If warning “This connection is untrusted”, click I Understand the Risks.
    • To suppress plugin warnings (not recommended):
      • Enter about:config in address bar.
      • Set extensions.blocklist.enabled to false.

Option 5: Clear Java Cache

If graphics fail to load after bypassing warnings:

  1. Open Java Control Panel → General tab → Temporary Internet Files → Settings.
  2. Uncheck Keep temporary files on my computer.
  3. Click OK and restart browser.
Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 13775
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore