I/A Series R2 Enterprise Server station is unable to connect to the SQL database

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series R2 Enterprise Server station is unable to connect to the SQL database
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • RyanSuar
    RyanSuar

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1333 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series R2 Enterprise Server station is unable to connect to the SQL database

Picard Product_Support
‎2018-09-10 02:33 AM

Issue

I/A Series R2 Enterprise Server station is unable to connect to the SQL database

The following errors are seen in the Enterprise Server station's Standard Output:

  • ERROR: Could not open database connection [/SQL2005/services/DatabaseService]
  • java.sql.SQLException: Charset 0x0904D00031/Cp850 is not supported by the JVM.

"The program can't start because MSVCR71.dll is missing from your computer. Try re-installing the program to fix this problem."

Environment

I/A Series r2.301.529

SQL Server 2005

Java Runtime Environment 1.6

Cause

JRE 1.4.1 which I/A Series R2 uses does not know how to support the CP850 character set.

Even though the computer has been installed with JRE 1.6, I/A Series R2 is still using JRE 1.4.1.

Resolution

To enable I/A Series R2 to use JRE 1.6, follow these steps:

  1. Download and install JRE 1.6 if it has not been already installed. The latest version can be found here http://www.java.com/en/download/manual.jsp.
  2. Go to Windows Services and stop the Niagara service.
  3. In Windows Explorer, go to \niagara\r2.301.529\nre\ and rename the 'jre' folder to 'jreold'.
  4. In Windows Explorer, go to C:\Program Files\Java (this is typically the path of the Java install). Copy the 'jre6' folder including its contents and paste it to the \niagara\r2.301.529\nre\ directory.
    Rename the 'jre6' folder to 'jre'.
  5. In Windows Explorer, go to \niagara\r2.301.529\nre\lib and open the 'nre.properties' file using a text editor program (eg. Notepad). Comment out the 'java.options...' parameter. Add the parameter shown below, save and close the file. Start the Niagara service and run the station. Check in the Standard Output window to see if the error has been cleared and that the DatabaseService has successfully connected to the SQL database.

    ########################################################
    #
    # File:  nre.properties
    #
    #    NRE properties
    #
    # Revision History
    #   21 Aug 03   Brian     Original version.
    #
    ########################################################

    # Virtual machine to use: jview|hotspot
    vm=hotspot
    #vm=jview
                         
    # List of Java options to pass thru to the VM (hotspot only)
    # Used with original install 1.4.1
    # java.options=-Xmx1024MB

    # List of Java options to pass thru to the VM (hotspot only)
    # USed with 1.6
    java -Xmx1G

 

Notes:

  • This solution can be applied to a similar error but with a different charset encoding error other CP850.
  • You may encounter the following error when you try to run WorkPlace Pro after performing this fix.

"The program can't start because MSVCR71.dll is missing from your computer. Try reinstalling the program to fix this problem."

To resolve this, go to \niagara\r2.301.529\nre\jre\bin and locate the file MSVCR71.dll. Copy this file to the C:\WINDOWS\system32 directory.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5993
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore