Issue
When adding a BACnet Binary Output object for a Functional Devices RIBTW2401B-BC RIB relay module in I/A Series R2, the device goes offline (status shows down). The output window displays:
ERROR: Unable to convert class tridium.foundation.dataspecies.DsEnum from ASN type 9
tridiumx.bacnet.asn.ASNException E_BACNET_ASN_INVALID_TAG {tagNumber 9 current tag 0}
BACnetDevice: RIB01 is now down
Product Line
TAC IA SeriesEnvironment
- I/A Series R2
- BACnet
- Functional Devices RIBTW2401B-BC
Cause
Resolution
- Disable the device ping mechanism in the I/A Series R2 UNC’s BACnet Service → Device Status tab.
- Reboot the UNC after making the change.
- Ensure you backup the station when prompted to save the configuration changes.