What I/A Series BACnet hardware (MNB) is officially UL 864 listed?
  • MNB
  • UL 864
Many consulting engineers would like documented proof that the hardware within a smoke control system is UL 864 tested and approved.
The Schneider Electric MicroNet BACnet UL 864 case file, outlining exactly what I/A Series BACnet hardware is approved for UL 864 systems can be obtained at:
  1. www.UL.com
  2. Navigate to the bottom of the home page under Useful links and click on Online Certifications Directory
  3. Find the UL File Number field and type s5381
  4. The Schneider Electric MNB file will show up and click the link UUKL.S5381 under the link to file column.
This will show you all of the I/A Series hardware that is UL 864 certified, and can be installed in an official smoke control system.
Also refer to the I/A Series MicroNet BACnet Smoke Control Systems Manual (F-27419) for further information related UL 864 Smoke Control applications.