How to write a program to monitor if a standalone CyberStation is offline?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to write a program to monitor if a standalone CyberStation is offline?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • BillNeville
    BillNeville
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1876 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to write a program to monitor if a standalone CyberStation is offline?

Picard Product_Support
‎2018-09-06 01:04 PM

Issue

Using the SendMail function in the NC2 and ACX2 to know if CyberStation is shut down would be a nice feature.

Environment

CyberStation

NC2, CX9680, bCX4040, bCX9640, ACX5720, ACX5740

Cause

When a standalone CyberStation is not monitored 24x7 and it is emailing critical alarms or pulling extended logs, it is important that it remains up and running as much as possible. How can the newer controllers' email capability be used to add this functionality.

Resolution

The SendEmail function can be used for this purpose.

  1. Set up the bCX via the "Email setup" controller webpage. This will require at least one Outgoing SMTP Server be accessible to your controller.
  2. The workstation commstatus is not a supported function within Plain English (although it may appear to compile in a program), so the workaround is to write a workstation program that sets a numeric in the controller on fixed timeframe. An InfinityProgram in the controller can monitor that numeric value and send the email if the value is not updated.
  3. Here are two sample programs for your use that provide a starting point for this application:

=======
'Fallthru program in CX triggered by minute which sends an email every 30 minutes while the workstation is offline
'Note: Set (Minute-Heartbeat) long enough for a CyberStation reboot/restart to avoid false alarms on an intentional shutdown. 

Checking:
If Minute = 10 and (Minute - WSHeartbeat) > 4 then goto Sending
If Minute = 25 and (Minute - WSHeartbeat) > 4 then goto Sending
If Minute = 40 and (Minute - WSHeartbeat) > 4 then goto Sending
If Minute = 55 and (Minute - WSHeartbeat) > 4 then goto Sending
Stop

Sending:
SendEmail('theemailaddresshere', Date, 'CyberStation is offline')
Goto Wait30m
 

Wait30m:
If TM < 29 then goto Wait30m

E:
If TS > 60 then Goto Checking
==========
==========
'Looping, autostart program in workstation

Wait30s:
If TS > 29 then goto SetRemoteFlag
 

SetRemoteFlag:
MyNetwork\My_bCX\WSHeartbeat = Minute
Goto Wait30s
 

E:
If TS > 2 then goto Wait30s
====== 

Note: For LAN Systems a workstation can monitor the other workstations using the CommStatus attribute.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 6617
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore