Issue
View the current firmware version on a Xenta controller using the RS-232 cable
Product Line
TAC Vista
Environment
- Vista 5.1.X
- Xenta Programmable Controllers
- Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B, 901
Cause
While it is the best practice to match all of the firmware versions in your controllers, this is a quick and easy way to view the current version installed on your hardware.
Resolution
- Connect the RS-232 programming cable to your controller and your PC
- Open TAC Tools 5.1.X
- Open Download Wizard
- Click next
- Click the information button located directly above the help button
For more information on how to update the firmware (.MOT file) on a Xenta controller, see Download an .MOT file into a Xenta Programmable controller.