How to view the current Priority level controlling an Analog BACnet object (AnalogOutput, AnalogValue) using Plain English.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to view the current Priority level controlling an Analog BACnet object (AnalogOutput, AnalogValue) using Plain English.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Carl_Slack
    Carl_Slack
  • AdamSteele
    AdamSteele
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1762 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to view the current Priority level controlling an Analog BACnet object (AnalogOutput, AnalogValue) using Plain English.

Picard Product_Support
‎2018-09-06 01:43 PM

Issue

How to view the current Priority level controlling a BACnet object using Plain English.

Environment

Continuum Cyberstation

BACnet

AnalogOutput, AnalogValue

Cause

3rd party is controlling a BACnet object at an unknown priority level. We want to see what the current Priority level is and relinquish this control.

Resolution

We can use the PriorityArray attribute to view the value of each Priority level. Then using a For loop we can loop through all 16 priority levels to determine the current priority level controlling the BACnet object.


Below is a program that will allow you to see the current priority (aaPriorityValue) controlling your object (PriorityTest) and at what priority level (aaPriorityIndex).

You will need to create two numerics (configure as AnalogValue) for this program to work (aaPriorityIndex and aaPriorityValue).

With the method below we can see if a non-zero value is the current priority and at what priority level.  Unfortunately a 0 value is seen the same as a NULL value (both seen as 0), so if a 0 value is currently controlling the object we are unable to determine at what priority level this is set.

If aaPriorityValue is 0 and aaPriorityIndex is < 16 then we know that aaPriorityIndex is the level of the non-zero value and can relinquish all priorities down to that level if needed. Still not exactly what we want but it does give a bit of flexibility to actually control the current priority level.

=======================
' Program to get the highest priority value and its index number
' Flow: Looping
Numeric count
Numeric PriorityValue

CALC:
  For count = 1 to 16   'Loop through the priority array, looking for the first non-Null value
    PriorityValue = ReadProperty(PriorityTest PriorityArray, count)
    If PriorityValue is not NULL then
      Break 'stop at the first non-Null value. Side effect, also first non-zero value
    Endif
  Next count

  If PriorityTest = 0 then
'Check for 0 value
    aaPriorityValue = 0
    aaPriorityIndex = count
  Else
'If not 0 or NULL value, set current priority value and index
    aaPriorityValue = PriorityValue
    aaPriorityIndex = count
  Endif
=================================


 

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5386
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore