Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to upgrade bin and SAV files in I/NET controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to upgrade bin and SAV files in I/NET controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
  • sesa139513
    sesa139513
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4769 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to upgrade bin and SAV files in I/NET controllers

Product_Support
‎2018-09-06 02:27 PM

Issue

How to upgrade the bin files and SAV files in controllers

Product Line

TAC INET

Environment

  • I/NET Seven 2.xx running in a Windows Environment.

Cause

The bin files for the controllers are not all current with the version of I/NET being used.

The SAV files backup process and what gets overwritten.

Resolution

To upgrade the bin files in the controllers:

  1. Attach to the controller by selecting from the pull down menu in I/NET, Connect and drill down past your link NPR to the controller
  2. Select Edit/Controller/Station Save – this backs up the current programming on the controller and overwrites your .sav file
  3. Select Edit/Host Computer/Software Restore and put a check in the box for Software and select the button for Download –this pushes the latest bin file to the controller.
  4. If you select the Database box in the previous step, it will push the database to the controller as well.
  5. If you have SCU or DCU controllers, select the SCU/DCU button at the bottom of the window from step 3 and follow the same procedure.
  6. Note: BIN files are stored in the C:\INET Seven Data\Data folder

 

To upgrade the SAV files in the controllers:

  1. Attach to the controller by selecting from the pull down menu in I/NET, Connect and drill down past your link NPR to the controller
  2. Select Edit/Controller/Station Save – this backs up the current programming on the controller
  3. sav files are located on the C:\Inet Seven Data\SAV folder.
  4. To make a backup, simply copy this folder to another location
  5. Step 2(two) overwrites the current SAV file in the c:\INet Seven Data\SAV location
  6. To restore the current SAV file to the controller, select Edit/Controller/Station Restore and overwrite the database in the controller

 

KEY POINT:

bin files are the software for the controller/device

.sav files are the database

Labels (1)
Labels:
  • TAC INET
Tags (5)
  • Find more articles tagged with:
  • 3922
  • db
  • firmware
  • i-net
  • upload
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore