How to upgrade TAC Vista 5.x.x SQL Database to 5.1.7

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to upgrade TAC Vista 5.x.x SQL Database to 5.1.7
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2253 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to upgrade TAC Vista 5.x.x SQL Database to 5.1.7

Picard Product_Support
‎2018-09-10 07:43 AM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:54 AM

Issue

Procedure to upgrade SQL database from TAC Vista 5.x.x to 5.1.7

Environment

TAC Vista 5.x.x

TAC Vista 5.1.7

MSSQL Express 2005 SP4

MSSQL Express 2008 R2 -SP1

Cause

Revised TAC Vista SQL database layout: TAC Vista 5.1.7 introduces a revised and improved SQL database layout in order to improve the overall performance in the TAC Vista system with large databases. The revised database layout is utilized by default for new installations and current installations can be upgrade either automatically or manually depending on the installation type.

SQL 2008 R2 Express SP1: Microsoft SQL Server 2008 R2 Express SP1 is now included in the TAC Vista Server 5.1.7 installer. The TAC Vista Server installer can upgrade an existing SQL Server 2005 Express installation to SQL Server 2008 R2 Express SP1; only supported in a typical TAC Vista installation.

 

 

Resolution

Follow the Instructions before Implementing this procedure:

  1. Take the Vista Backup and SQL DB backup before implementing this process.
  2. Shutdown the TAC Vista Server. If the Vista Server running as a Server, Stop the service and shutdown the TAC Vista Server.
  3. Open the “SQL Database Upgrade 5.1.7” (From Program Files [or] from Start Menu)


     
  4. Check the Server and Database options.

     
  5. Choose the correct type of Authentication. If the vista using SQL Server, choose the SQL Server Authentication, enter the correct Login details.
     
  6. Click on “Test Connection” and “Test User access”. You should find Test Connection access and Test User access successful.
  7. If Vista and SQL DB backup has taken, check on the “Check Box”.


     
  8. Click on “Upgrade”, then the following screen appear. Then Click on “YES” to upgrade.


     
  9. After the upgrade is complete check the Vista Server has a connection to the upgraded SQL database. This is done from the Vista server setup. Use the test connection

  10. If the connection is successful you will see a message like this.



     
  11. Now, the SQL database has been upgraded.

Download this procedure in PDF Here .

Labels (1)
Labels:
  • TAC Vista
Attachments
Tags (1)
  • Find more articles tagged with:
  • 7445
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore