Issue
How to set an LNC-100 back to factory-default settings. This will erase all block programming and device configuration.
Environment
Network 8000 LNC-100 and related controllers based on the GCM-861X0 series platform, including the GCM-86110,
GCM-86120, SIM-CCN, SIM-MTECH, SIM-TRANE, and SIM-YORK
Cause
Sometimes it is necessary to manually clear the controller EEPROM in order to reload a database.
Resolution
Follow the steps below: Backup the controller database. Clear the controller's EEPROM. This is accom...