How to relinquish a priority on multiple BACnet objects from a list view or search
  • How to relinquish a priority on multiple BACnet objects from a list view or search
  • Cody_Failinger
    Cody_Failinger
  • AbeMeran
    AbeMeran
‎2018-09-11 01:39 PM
How to relinquish a priority on multiple BACnet objects from a list view or search.
  • Workstation
  • Automation Server
  • Enterprise Server
Need to relinquish a value in the priority stack for multiple points at once.
  1. In the list view or search select all of the objects in question (IMPORTANT: Only objects of the same class type should be selected)
  2. Open the property grid by clicking the red check mark.
  3. Go to the Command tab and remove the value from the priority that is to be relinquished then save the change
NOTE: As of 1.5 the above steps work ONLY for objects of analog type.mass-relinquish.png
In the screen shot above:
  1. Use back space to remove the 1, leaving the field blank
  2. Save the change
  3. SBO will relinquish priority 16 on all the objects selected in the list view or search.