Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How to redirect a offline alarm to a certain alarm control object in Vista?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to redirect a offline alarm to a certain alarm control object in Vista?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Jonas_Brissman
    Jonas_Brissman
  • Benji
    Benji
  • sesa150555
    sesa150555
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1511 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to redirect a offline alarm to a certain alarm control object in Vista?

Picard Product_Support
‎2018-09-06 03:32 PM

Issue

Is it possible to redirect all offline alarms to a certain alarm control object in Vista?

Environment

Vista 5.1.7

Cause

Using the "Configure alarm" function in the Vista server all offline alarms can be sent to a special alarm control object in Vista.

Resolution

Start with creating a new Change of state object in Vista

To create a Change of State

  1. Right-click the Vista server node/object
  2. Point to New, point to Object, and then click "Change of State - System".
  3. Type the name. In the example, "Offline_Alarms".
  4. Right-click the newly created Change of State object. In the example, Offline_Alarms.
  5. Click Properties.
  6. Type a descriptive text. In the example, "Handles alarms for devices going offline".
  7. Change the priority. In the example, change the priority to 1.
  8. On the Alarm tab, in the Alarm processing control box, type the name of the alarm control object for priority 1 alarms. In the example, Alr_Cntrl1.
  9. Click OK.

Filtering and Linking an Alarm

We can now filter out system alarms ($EE_Mess messages) tripped by devices going offline. The alarm texts contain the word "Offline" and we use this as the filter.

To filter and link an alarm

  1. On the Windows task bar, click TAC Vista Server.
  2. On the File menu, click Log in and log in.
  3. On the Configure menu, click Configure Alarms.
  4. Click Add.
  5. In the Text match box, type the filter mask. In the example, "*Offline*".
  6. In the Event object box, click Browse.
  7. In the Units list, browse to the Change of State – System object.
  8. In the Objects list, click the Change of State – System object. In the example, Offline_Alarms.
  9. Click OK.
  10. Minimize Vista Server. When a Xenta device goes offline, a priority 1 alarm appears. The alarm is handled by the Alr_Cntrl1 object
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 7557
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore