How to prevent BACnet client from triggering EBO backup

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to prevent BACnet client from triggering EBO backup
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran
  • Mahmoud_Sayed
    Mahmoud_Sayed

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1243 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to prevent BACnet client from triggering EBO backup

Captain AbeMeran Captain
‎2023-04-13 04:41 PM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-10-16 07:46 AM

Issue

Any third party BACnet client can initiate an EBO backup.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server

Cause

As of EBO 2023 (5.0.2.109), EBO's BACnet backup operation requires no password which means any BACnet client with the EBO server BACnet interface's device ID can initiate an EBO backup without any restrictions.

Any such backup can be identified by looking at the backup description in EBO, the backup will explicitly indicate that it was generated by third party BACnet Workstation.

2023-04-05_14-22-29.jpg 

Resolution

EBO 2024 (V6.0.1) or higher:

In BACnet Interface basic tab, "Restrict backup and restore service" can be set to Yes to ensure that third-party BACnet clients cannot perform a BACnet backup or restore on the EcoStruxure BMS server. Refer to: BACnet Interface for an Automation Server – Basic Tab and BACnet Interface for an Enterprise Server – Basic Tab

Mahmoud_Sayed_0-1729089830560.png

 

EBO 2022 (4.0.4CP2 or higher) and EBO 2024 (V5.0.3 or higher):

A rule can be added to the BACnet service_blacklist to disable BACnet backup service.

See https://community.se.com/t5/Building-Automation-Knowledge/BACnet-RULES-implementation-to-disable-fea... for details on how to create service_black list.

 

Use the following syntax to create a rule that restricts BACnet back up initiated by 3rd party BACnet client on the EBO server.

 

<blacklist>
<global>
<restrict-backup-service/>
</global>
</blacklist>

 

Any BACnet client requesting backup from EBO server configured with the above rule will be presented with error similar to screenshot below.

2023-04-05_08-33-24.jpg

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (8)
  • Find more articles tagged with:
  • AbeMeran23
  • backup
  • bacnet
  • blacklist
  • MahmoudSayed24
  • rule
  • rules
  • service_blacklist
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore