How to move a CyberStation installation when replacing the workstation PC on a LAN system.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to move a CyberStation installation when replacing the workstation PC on a LAN system.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1679 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to move a CyberStation installation when replacing the workstation PC on a LAN system.

Picard Product_Support
‎2018-09-06 01:12 PM

Issue

What is the procedure on transferring Continuum from one PC to another PC?
 

Environment

  • Cyberstation
  • SQL

Cause

Workstation hardware must be replaced.

Resolution

Collect information from the existing machine

  • Backup the Continuum Database
  • Collect all IP address, DNS server and WINS server IP information from the existing workstation.
  • Determine if the workstation was a member of a network domain and record the domain name. 
  • Run Continuum Database Initialization on the existing machine.
  • Select Workstation.
  • Record the following information.
    • Workstation Name
    • Folder Name
    • Device Node ID
    • Network ID
    • Data Source Name
    • Database Name
    • User Login ID
    • Server Name.
  • Verify that you have the correct database User Password.
  • Start Continuum and run PinPoint.
    • From the View menu select Options
    • Record the folder path indicated under Graphics (Pin Files):.
    • Record the folder path indicated under Image:.
    • Record the folder path indicated under Background:. 

Install CyberStation on the new machine

  • Before removing the existing machine from the network, start the new Workstation without connecting it to the network.
  • Log on to the PC using an the Local Administrator password.
  • Configure the IPaddress, DNS server and WINS server IP address collected from the existing machine.
  • Disable all Virus protection software.
  • Turn off all FireWalls (Windows 7 has three firewalls).
  • On Windows 7 machines disable Windows Defender.
  • On Windows 7 machines shut off SPS Software Protection Services.
  • Install Cyberstation on the new Workstation PC
  • Shut down the PC.

Note: Do not run Continuum Database Initialization at this point.

Swap the workstations

  • Shutdown the existing workstation and remove it from the network.
  • Connect the new workstation to the network
  • Start the computer.
  • Log on to the computer using an Administrator level user account.
  • If the existing workstation was connected to a network domain, join the network domain.
  • Verify that you have full network connectivity by pinging known ethernet addresses.

Update the Continuum Database.

  • Run Continuum Database Initialization.
  • Select Workstation.
    • Enter the information under Workstation using the information collected on the existing machine and apply changes.
    • Launch Continuum CyberStation and verify that Cyberstation is working properly.
  • Run PinPoint
    • From the View Menu select Options
    • Enter the pinpoint file path location collected from the existing workstation.
    • Select the Checkbutton and verify that a failure notice (a red "X") does not appear beside any item.
    • Apply changes.
  • Verify that all Continuum functions are operating as expected.
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 6332
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore