How to identify Automation Server(AS) ID node count
  • How to identify Automation Server(AS) ID node count
  • StephenYang
    StephenYang
Admiral StephenYang Admiral
‎2025-06-30 07:47 AM
on ‎2025-06-30 07:47 AM
Fail to apply CP or HF on AS
  • EcoStruxure Building Operation Workstation
  • EcoStruxure Building Operation Automation Server (ASP/ASB)
The Automation Server is not installed next to the Power Supply.
The requirement is stated in the Hardware Reference Guide, Position 1 is reserved for a power supply. Position 2 is reserved for an automation server.
When the update process fails, please collect the DebugInformation.
Next, check the System.log for the node ID.
  • If the node ID is not 2, it indicates that the AS is not installed at the correct address.
  • In that case, the physical location of the AS needs to be corrected.
Example of incorrect ID location
Relevant Resource:
Multiple Automation Servers on the same backplane
  • StephenYang25
100% helpful (1/1)