How to decrypt bit information of a xDriver point (Integer/Word) value.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to decrypt bit information of a xDriver point (Integer/Word) value.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • SangKim
    SangKim
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1436 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to decrypt bit information of a xDriver point (Integer/Word) value.

Picard Product_Support
‎2018-09-06 01:40 PM

Issue

Most of the xDriver points provide bit (binary) information in a word(integer) point in order to save register address. In order to interpret/decrypt the bit information out of the word(integer) value, PE programming is required.

Environment

Net Controller (CX99xx, CX96xx)

bCX controller (bCX4040)

ACX5740/5720

Cause

Bit information is displayed as a number in the controller when read in to.  Need to have PE function to decrypt the number in to each bit information.

Resolution

Create InfinityProgram in the Controller as below;

' = = = = = = = = =
Numeric locNum1
Numeric nBit0, nBit1, nBit2, nBit3, nBit4, nBit5, nBit6, nBit7, Numeric nBit8, nBit9, nBit10, nBit11, nBit12, nBit13, nBit14, nBit15
Line ReadAndSet
  locNum1 = CIAlarms ' Read the xDriver point and set to local point.
  Goto AAA
Line AAA
  ' Decrypt each bit information from the locally mirrored point.
  nBit0 = (locNum1 bitand 2 ^ 0) > 0  
  nBit1 = (locNum1 bitand 2 ^ 1) > 0 
  nBit2 = (locNum1 bitand 2 ^ 2) > 0 
. . . . . 
  nBit15 = (locNum1 bitand 2 ^ 15) > 0 
  Goto BBB
Line BBB
  ' Do something here for each nBit0~nBit15 such as below
  ' If nBit0 then
  ' set InverterTempAlarm = On   'Set the global point to ON
  ' Else
  ' set InverterTempAlarm = Off   'Set the global point to OFF
  ' Endif
  . . . . . .
   Goto CCC
Line CCC
  ' Wait for 15 seconds and send to the first line to read the xDriver point again.
  If TS < 15 then Goto CCC
  Goto ReadAndSet
Line E
  If TS < 30 then Goto E
  Goto ReadAndSet

' = = = = = = = = =

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5472
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore