Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

How to create i2xxx and b3xxx controllers from a CSV dump file.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to create i2xxx and b3xxx controllers from a CSV dump file.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AdamSteele
    AdamSteele
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1780 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to create i2xxx and b3xxx controllers from a CSV dump file.

Picard Product_Support
‎2018-09-06 10:54 AM

Issue

How to create i2xxx and b3xxx controllers from a CSV dump file.

Environment

Continuum

i2xxx Controllers

b3xxx Controllers

Cause

In this scenario they wanted to create the beginning of a site database from CSV dump files before deploying on site. 

Resolution

It seems that when creating an i2 or b3 object, the path is also required when defining the comm port. Make sure to add the path to the Port field and this should allow the controller object to be created. See the original CSV I exported below, how it was modified, and then imported back in successfully.

Original Export to CSV

InfinityInfinetCtlr
Name,InfinetId,Port,DeviceId,SerialNum,Alias,CntrlType
i2_850,32,Comm1,Network1\ACX11_10th,11111,i2_850,i2920

Modified Import CSV

InfinityInfinetCtlr
Name,InfinetId,Port,DeviceId,SerialNum,Alias,CntrlType
i2_920,32,Network1\ACX11_10th\Comm1,Network1\ACX11_10th,11111,i2_920,i2920

Now, this import does complain about the CntrlType in the distribution Properties window but does create the controller and sets the type correctly. If you don't want any errors you can remove the CntrType attribute and the controller object will still be created but will default to a 240 controller. See below.


Import CSV without CntrlType

InfinityInfinetCtlr
Name,InfinetId,Port,DeviceId,SerialNum,Alias
i2_920,32,Network1\ACX11_10th\Comm1,Network1\ACX11_10th,11111,i2_920
 

This can then be changed to whatever controller you require through the controller Device object dialog.
 

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 11741
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of