How to copy Xenta 102-AX parameters between controllers in NL220
  • How to copy Xenta 102-AX parameters between controllers in NL220
  • PeterLarsen
    PeterLarsen
‎2018-09-10 03:50 AM
Is there a way to copy the setup parameters from one Xenta 102-AX VAV controller to another?
  • Xenta 102-AX
  • NL220
To assist in commissioning of many Xenta 102-AX controllers with similar configurations, parameters can be copied between controllers.
  1. Locate the controller you want to copy the parameters from.
  2. Right click on the controller and select "Copy configuration values to memory"
  3. Locate the controller you want to paste the parameters into.
  4. Right click on the controller and select "Paste configuration value(s) from memory"
  5. Then modify the parameters for that specific 102-AX as normal.
  • 6530