Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How to configure an alarm to see when controllers go offline.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to configure an alarm to see when controllers go offline.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AdamSteele
    AdamSteele
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2212 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to configure an alarm to see when controllers go offline.

Picard Product_Support
‎2018-09-06 01:32 PM

Issue

How to configure an alarm to see when controllers go offline.

Environment

Continuum

Continuum Controllers

Cause

Want to see an alarm when controllers go offline / online.

Resolution

There is a default EventEnrollment already created that does this.

To setup controller offline alarms, do the following:

  1. Go to the "Templates" folder in Continuum Explorer where a number of default EventNotifications are found.
  2. Open the "ControllerStatus" EventNotification and go to the Delivery tab.
  3. Add in the Workstations that where this alarm is to be sent too.

Now any time a controller goes offline or comes back online, an alarm entry will be received at the Workstation entered in step 2.

The other EventNotifications in this folder can be used to provide alarms on the subnet controllers status (InfinetStatus), IOU modules (IOModuleStatus), etc...

***Important:

CyberStations detect controller’s offline status via a mechanism that periodically probes the controllers for their communication statuses; the default period for the probe is 60 seconds. If data is consistently being passed then no probe goes out. A Probe will go out if the controller has not heard from the other controller after a minute and no data has been passed. If an ACK is not received then it will try 3 more times with a 5 second delay after each retry. If it does not get a response after the 3rd retry then it will mark the controller offline and register a node failure alarm.

If a controller goes offline for a short period of time (60 seconds or less) it is possible that not all recipient CyberStations will see the controller offline. If the CyberStation designated as the logging CyberStation for the ‘ControllerStatus’ alarm misses the offline condition the alarm WILL NOT be logged in the database.
 

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5716
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of