How to clear the error log in the Continuum controllers.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to clear the error log in the Continuum controllers.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1729 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to clear the error log in the Continuum controllers.

Picard Product_Support
‎2018-09-06 10:45 AM

Last Updated: Administrator CraigEl Administrator ‎2024-05-12 06:55 PM

Issue

For various reasons sometimes it is necessary to clear the error log in the controllers.

 

NOTE: First generation controllers such as the CX9200 and CX9900 (NetController 1) and Infinet1 devices do not support the error log utility, this article does not apply to those controllers.

 

Product Line

Andover Continuum

Environment

  • CyberStation
  • bCX9640
  • bCX4040
  • bCX4000
  • CX9680
  • ACX5740
  • ACX5720
  • All b3 devices
  • All i2 devices

Cause

Guidelines for clearing the controllers error log in the field.

Resolution

bCX4040, bCX4000, b3s

Error log is cleared by setting the Errors system variable to 0 (zero)

 

IMPORTANT

It s not recommended to set the errors system variable from within a Plain English program, doing so risks damaging the controller's flash memory which has a limited number of write/erase cycles. Only reset the errors system variable to 0 from the command line or from the system variable object editor.

 

If the Errors system variable has a non zero value all that is required is to reset it to 0

 

NOTE:

In some older version of the firmware, if the Errors system variable is at 0 then it has to be changed to a non zero value before it can be reset to 0

One easy way to generate an error is to create an InfinityProgram that attempts a DIVIDE BY ZERO

I.e.

Program is AutoStart and FallThru

Numeric N

n = 1/0

 

Create the InfinityProgram above in the controller, once the program saves and runs it will be disabled and the Errors system variable will increment by one.

Remember to delete the program as it is no longer needed


bCX9640 CX9680, ACX5740, ACX5720

Use the controller error log tool to clear the error log.

Labels (1)
Labels:
  • Andover Continuum
Tags (3)
  • Find more articles tagged with:
  • 12189
  • AbeMeran24
  • errorlog
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of