Issue
When assigning a schedule to a personnel area located in a different Continuum network than the door, the schedule does not function as expected.
Product Line
Andover Continuum
Environment
- ACX5740
- ACX5720
- Continuum Access Control systems with multiple networks
Cause
Objects cannot be passed between different Continuum networks. A schedule linked to a personnel area assignment must reside in the same network as the door that uses the area.
Resolution
Ensure that the schedule is located in the same network as the door requiring the area assignment.
Best Practice:Place schedules within the controller for the door. This ensures that if the controller goes offline, the schedule will still operate correctly.