Issue
You need to transfer your MicroNet View license from an existing PC to a new one.
Product Line
Satchwell MicroNetEnvironment
MicroNet View
Cause
Migration of MicroNet View software and license due to hardware upgrade or replacement.
Resolution
On the Existing Computer
- Close MicroNet View and all associated programs.
- Navigate to:
C:\MicroNet\Binary\VCommon\License
and copy theWWSUITE.LIClicense file. - Navigate to:
C:\MicroNet\Projects
and copy your MicroNet View project files. - Remove the MicroNet View dongle and I/O server dongle from the parallel port.
On the New Computer
- Install MicroNet View.
- If using Windows XP, install the Hasp dongle driver from the Hasp folder on the MicroNet View installation CD.
- Plug in both dongles to the manufacturer’s standard parallel port.
⚠️ Note: Add-on parallel port cards may not recognize the dongles.
- Copy the
WWSUITE.LICfile to:C:\MicroNet\Binary\VCommon\License - Copy your project files to:
C:\MicroNet\Projects - Reboot the computer.
- Launch the Project Manager:
C:\MicroNet\Binary\Project\MNProject.exe - From the menu, select:
“Find and register a project” - Locate and highlight your project, then click OK.
- You should now be able to run your MicroNet View project on the new computer.