Issue
Product Line
TAC IA SeriesEnvironment
I/A Series Niagara r2
Cause
Resolution
-
Stop the Niagara Service
- Open Services in Windows and stop the Niagara service to prevent conflicts during removal.
-
Delete the Version Folder
- Navigate to the installation directory (e.g.,
C:\Niagara\) and locate the folder corresponding to the version you want to remove (e.g.,r2.301.xxx). - Delete this folder.
- Navigate to the installation directory (e.g.,
-
Optional Cleanup
- Verify that no shortcuts or registry entries remain.
- Restart the PC to ensure all changes take effect.