Need a fast and efficient way to lock down multiple areas in one operation when a threat is perceived at a site.
The Continuum Physical Access Control System supports an advanced feature that allows for quickly locking down parts of or an entire building or campus via the areas/doors that are under physical access control by the Continuum system.
This functionality is available in second-generation access controllers such as the CX9680 (NC2) and the CX5720/5740(ACX2)
In Continuum, lockdown of an area or door means that access to the area/door via the physical access control system is restricted in such a way that prevents the movement of individuals into the locked-down area/door as well as keeping individuals from leaving the area/door under locked down.
Locking down an area automatically locks down all doors associated with the area; Continuum also allows doors to be
locked down individually.
When a door/area is locked down, all credential access attempts and exit requests are denied. The only way to gain
access into the locked-down door/area is by the use of a credential that has been designated with ‘Executive Privilege’ in the system. Note though, that a person with executive privilege may gain access into a locked-down area/door via the credential reader but if the mode of egress from the area is via Exit Request then such person would not be able to exit the door thru the normal exit request mechanism as there is no way for the person to indicate her ‘executive’ privilege by any means other than presenting the proper credentials (card or PIN) at a reader.
This document outlines several methods of implementing area lockdown for a building or campus such as a school, the methods outlined in the document are provided for illustration purposes only and are not to be taken as a complete solution but rather as general guidelines.
On legacy controllers that do not support the Area Lockdown feature (CX99xx, ACX7xx), we can still secure the doors by setting their state to disabled which prevents the doors from processing credential access attempts as well as Request to Exit, please note that in this case, NO ONE (including executive privilege personnel) will be able to gain access to the door until it is re-enabled
How to Lockdown your facilities using Continuum area lockdown outlines several methods of implementing area lockdown for a building or campus such as a school, the methods outlined in the document are provided for illustration purposes only and are not to be taken as a complete solution but rather as general guidelines.