How to Identify BACnet Instance Numbers in Niagara R2 UNC-520

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to Identify BACnet Instance Numbers in Niagara R2 UNC-520
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • sesa116873_brid
    sesa116873_brid

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1261 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to Identify BACnet Instance Numbers in Niagara R2 UNC-520

Picard Product_Support
‎2018-09-06 01:02 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 04:02 PM

Issue

When adding more BACnet objects to a Niagara R2 UNC-520, users need a way to generate a report listing all BACnet object instance numbers currently in use.

Product Line

TAC IA Series

Environment

Niagara R2 all versions

Cause

Niagara R2 does not provide a built-in feature or report to list BACnet instance numbers assigned to objects in a UNC.

Resolution

The only available method is to manually search the station’s XML configuration file for the term instanceNumber.

Steps:

  1. Locate the station XML file on the UNC.
  2. Open the file using a text editor.
  3. Search for the keyword:
    instanceNumber
    
  4. Review the results to identify all BACnet object instance numbers currently assigned.

Best Practices for BACnet Instance Numbers

  • Use Unique IDs Across the Network
    Ensure each BACnet object has a unique instance number to avoid conflicts during device discovery.
  • Follow a Logical Numbering Scheme
    Assign ranges per device type or location (e.g., 1000–1999 for AHUs, 2000–2999 for VAVs).
  • Document Assigned Ranges
    Maintain a central record of instance number ranges for all devices in the project.
  • Avoid Overlapping Ranges
    When adding new devices, verify that the chosen range does not overlap with existing assignments.
  • Plan for Future Expansion
    Reserve gaps in numbering for anticipated future devices or points.
Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 6664
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore